JayL
 JayL
(@jayl)
Posts: 5426
Member
Topic starter
 

Some of our resident engineers and fellow DIYers probably can answer this.

Can a 3000 watts generator power a house. If so what can it supply.

Question was asked by a friend in the US. He wants to send a generator for his house in the province.

Just making sure I get more hands on feedback before I reply.

Thanks a lot for any insights.

Jay

Millermatic 180 Autoset Mig Welder
Miller Spoolmate 100 Spool Gun
Victor Firepower 350 Oxy Ace Outfit
3M Speedglas 9002X AD Helmet
Makita LC1230 Dry Cut Saw
Ingersoll Rand Air Tools
Snap On Tools
Metabo Power Tools
Norseman Drill Cutting Tools
Bosch Power Tools
3M PPS

 
Posted : 17/05/2011 3:08 am
violaine
(@violaine)
Posts: 1926
Noble Member
 

Re: Generators

models available for household use typically are between 3 to 8 HP producing 500 to 4000 watts of power.

several factors to consider when selecting a generator...firstly the total estimated consumption on all electrical appliance including light fixtures...and of course if we are a woodworker, the power tools.

the wattage rating of a generator refers to its continuous running wattage..although all models feature a surge or max rating as much as 25 percent higher than the running value, you should rely on the running wattage rating when choosing one. a generator with more power than you need will run more smoothly for longer stretches and require less maintenance.

most generators are equipped with 1 to 4 outlets (with 120 and 240 volts too)..the generator should have an effective muffler as well..coz you dont want to have sleepless nights while hearing the roaring sound of it...unless you want to splurge on cables..tank fuel is another consideration...it should at least run for 90 minutes full tank.

shown below is the typical power tool wattage ratings

Tool Watts (start up) Watts (running)
Table saw 4000 1500
Circular saw 2500 1200
Router 1 1/4 HP 900 700
Electric drill (1/2) 800 600

The devil will find work for idle hands to do.-Morrissey

 
Posted : 17/05/2011 4:14 am
rosy
 rosy
(@rosy)
Posts: 4307
Member
 

Re: Generators

Yes that 3000 watt genset can power up a whole house but that will depend on the kind of appliances they will use. As long as the total amount of wattage will not exceed the specified wattage indicated on the genset.

It can power two or three electric fans, several fluorescent lights or cfls, a computer, a refrigerator, a television and possibly a small washing machine. Basta any low-wattage appliances will do. See here I never mentioned an up right freezer or a chest freezer or an airconditioner unit.

Mine I use it only during stormy months when brown-outs happen during or after a strong typhoon. I use it also to power my electric deep well pump to fill up my concrete water reservoir. :p

If the 3000 watt genset has a large capacity fuel tank, then it can run up to 10 to 12 hours non stop but if the load is reduced to lets say 30% or 50%, engine will run smoother and longer.

Basically it will be sufficient enough for some lights, electric fans and a ref to continually preserve food. :banana1: :2thumbsup: :barmy:

CIGWELD Weldskill 250 amp Mig Welder
AHP Alpha-TIG 200X welder
HITRONIC 300 Amp DC Inverter IGBT Welder
YAMATO 300 amp AC Stick Welder
YAMATO 200 amp DC Inverter IGBT Welder
DeWALT Chopsaw
HOBART and ESAB Welding Helmets
cloned STIHLs
MS 044 chainsaw
MS 070 chainsaw

 
Posted : 17/05/2011 10:03 am
jarod
(@jarod)
Posts: 1222
Noble Member
 

Re: Generators

Will it be used for daily use or as an emergency power source only?

For more of the latest tools, deals and tips - click HERE

 
Posted : 17/05/2011 11:16 am
JayL
 JayL
(@jayl)
Posts: 5426
Member
Topic starter
 

Re: Generators

Will it be used for daily use or as an emergency power source only?

Good question Jarod. I'll ask my friend.

In your opinion will 3000 watts be good for continuous use?

Thanks

Millermatic 180 Autoset Mig Welder
Miller Spoolmate 100 Spool Gun
Victor Firepower 350 Oxy Ace Outfit
3M Speedglas 9002X AD Helmet
Makita LC1230 Dry Cut Saw
Ingersoll Rand Air Tools
Snap On Tools
Metabo Power Tools
Norseman Drill Cutting Tools
Bosch Power Tools
3M PPS

 
Posted : 17/05/2011 3:36 pm
bmac
 bmac
(@bmac)
Posts: 114
Estimable Member
 

Re: Generators

Some of our resident engineers and fellow DIYers probably can answer this.

Can a 3000 watts generator power a house. If so what can it supply.

Question was asked by a friend in the US. He wants to send a generator for his house in the province.

Just making sure I get more hands on feedback before I reply.

Thanks a lot for any insights.

Jay

Yes. but that will depend on the electrical load.

steps in selecting your genset.

1. base load or back up only
2. whatever you choose from #1. calculate your estimated consumption including future electrical load
3. choose a genset that is twice the calculated load. to make it 50% of the genset capacity
4. congrats! yun lang

 
Posted : 17/05/2011 4:23 pm
jarod
(@jarod)
Posts: 1222
Noble Member
 

Re: Generators

Good question Jarod. I'll ask my friend.

In your opinion will 3000 watts be good for continuous use?

Thanks

It would still depend on what will they be using, the power requirement will dictate how many KVAs(KiloVolt-Amps: unit more used in generators) is needed.

3000W is just equal to 3 hot irons :rolleyes:

Heating/heat converting appliances are the most power-hungry items in the house so identification, computation and additional overhead is needed to identify what would generator rating would satisfy their needs.

For more of the latest tools, deals and tips - click HERE

 
Posted : 17/05/2011 6:06 pm
(@willyfernando)
Posts: 799
Prominent Member
 

Re: Generators

Good question Jarod. I'll ask my friend.

In your opinion will 3000 watts be good for continuous use?

Thanks

Most portable gensets range from 2KVA up to 10KVA. Standard load like lighting, electric fans and refrigerators are not an issue for these type of generators. What you have to watch is the sensitive load that we sometimes forget to consider. Electronic items like Laptops, PC's celphones and semicon based products w/ have a different power signature or sine wave, etc. You may have to consider a genset w/ a built in Voltage Regulator or AVR in their system coz I've seen many cases of fried electronics right after genset power kicked in.:eek::eek::yikes::oops:

 
Posted : 18/05/2011 7:20 am
(@yong2x)
Posts: 15
Active Member
 

Re: Generators

Sir JL,
If he has a house in the province, most likely they have electric power there. We do have relatively stable power in the Philippines. If he sends a 3KWatt gen set here (from the US) then chances are they are rated for 110VAC - we use 220VAC so to use that to power his house may require a little more than just wiring. He could technically provide a new set of electrical connections for lights run by the gen set or some 110VAC outlets as well.

Now if for some reason the gen set is capable of getting out 60Hz, 220VAC then I would just want to connect it to the circuit for lights only and no outlets. 3KW is just to small to guarantee I get all normal household appliances to run and without power conditioning it may be detrimental to the appliances too.

What I would suggest is get a good car battery charger (one that can charge several gangs of batteries at once), get several car batteries, and get a good inverter. Since we have a relatively stable power supply, we can continuously charge the batteries and when there is power interruption, you can use the batteries with the inverters to run lights and appliances. For really demanding appliances, you can get the more expensive TRUE SINE WAVE inverters. No noise, no need for gasoline, no pollution but there is the possibility of battery acid spillage that needs to be managed.

You can also charge your neighbor's car batteries for a fee 🙂

 
Posted : 18/05/2011 9:34 am
 wool
(@wool)
Posts: 59
Trusted Member
 

Re: Generators

Yes. but that will depend on the electrical load.

steps in selecting your genset.

1. base load or back up only
2. whatever you choose from #1. calculate your estimated consumption including future electrical load
3. choose a genset that is twice the calculated load. to make it 50% of the genset capacity
4. congrats! yun lang

I am planning to buy a Australian surplus 720watts petrol generator
1.backup generator and out of town trips portable power(twice a year at most)
2. loads would be phone chargers(15w)/laptops (65w) / lighting no more 30watts
3. 720 watts would sufficient enough for powering those.

if you run the generator at 50% capacity would it still consume the same gasoline running at 90% capacity?

 
Posted : 08/02/2012 5:02 pm
(@bryant77)
Posts: 480
Reputable Member
 

Re: Generators

Same lang ang gasoline consumption either you use 50% or 90% of load capacity of the generator

 
Posted : 08/02/2012 8:07 pm
 wool
(@wool)
Posts: 59
Trusted Member
 

Re: Generators

thanks bryant77. I will just use my omni power reader to efficient use the generators power output

 
Posted : 10/02/2012 4:35 pm
(@vrcinfo)
Posts: 95
Trusted Member
 

Re: Generators

I had ones imported a generator from Saudi when I was an OFW. During the 90's there were frequent brownouts so it was nice to have one. But as time goes by and brownouts were so seldom that maintaining a generator is difficult. Gasoline gets stale easily and gets water vapor in the tank while stored. This makes starting the genset very very difficult. Unless you change the gasoline often or put a fuel stabilizer and start you genset regularly. Its good if its a diesel genset as i believe it doesn't get stale often as gasoline. Now i use an inverter to power my house during brownouts. I get my power source from my cars 12V battery. I turn-off the main breakers, unplug the ref and plug my inverters output to a wall socket. Depending on the rating of the inverter its good enough to run the elec. fan, LCD TV and lighting system, and there's no noise that's so bothering. By the way, I change all my light bulbs to LEDs. Inverters normally have a warning sound and automatic cut-off in case of overload. And they are getting cheaper now.

 
Posted : 10/09/2012 5:38 pm
(@kenneth)
Posts: 51
Trusted Member
 

Re: Generators

I have a diesel generator. I have maybe 50 liters of diesel that's been sitting around in gas cans for the past 2 years. Does diesel go bad? If so, how can I dispose of it properly?

 
Posted : 04/02/2013 4:16 am
rosy
 rosy
(@rosy)
Posts: 4307
Member
 

Re: Generators

Hi there Kenneth,

WOW, how come you have that much diesel fuel in your place.

Yes bro diesel fuel do go bad and change after being stored after more than a year, it starts developing gum like residue underneath plus if stored in drums or cans, it develops some chemical reaction, also develops some reaction during cold weather but I guess it will not be so much since it is always warm or hot here in our country. Better if it was contained in a thick plastic container/drum. 😉

How to dispose of it, sell it to jeepney drivers, they will be happy to buy it from you perhaps not using the prevailing price of diesel in gasoline stations. Better dispose of it soon and just buy new supply only as needed. :p

CIGWELD Weldskill 250 amp Mig Welder
AHP Alpha-TIG 200X welder
HITRONIC 300 Amp DC Inverter IGBT Welder
YAMATO 300 amp AC Stick Welder
YAMATO 200 amp DC Inverter IGBT Welder
DeWALT Chopsaw
HOBART and ESAB Welding Helmets
cloned STIHLs
MS 044 chainsaw
MS 070 chainsaw

 
Posted : 04/02/2013 9:52 am
Page 1 / 3
Share: